NJ Fishing Advertise Here at New Jersey's Number 1 Fishing Website!


Message Board


NJFishing.com Your Best Online Source for Fishing Information in New Jersey - View Single Post - electrical breaker problem
View Single Post
  #7  
Old 02-13-2014, 12:09 PM
Capt. Debbie's Avatar
Capt. Debbie Capt. Debbie is offline
NJFishing.com Old Salt
 
Join Date: Mar 2008
Location: Suffern NY / Sandy Hook
Posts: 2,604
Default Re: electrical breaker problem

You may not have fortitude for this to see if actual overload or not.

Disconnect one line into breaker. Load side is best. With load wire off the breaker, CLOSE the 40amp breaker. Should be 0 amps and nothing happens. Then slowly use needle nose to touch the load wire to empty close breaker side. If it is really over 40 amps ( a lot of current ) you will see a visible spark as you touch before the breaker pops.

If no spark it is NOT anywhere near 40 amps or over. In fact where you touch that load wire will likley have a black burn mark or more where it was touched with that kind of current.

In case you're wondering the wire you're holding is a load and if you drop it nothing happens.

Breakers pop proportional to the overload. They are made to driefly run with slight overload and pop immediately with big overloads like dead shorts.

So a 40 or 42 amp load on a breaker can take minutes to pop. While a 80 or 100 amp short will pop the breaker in a fraction of a second.

Hope that helps you?
__________________
Capt. Debs
Tow boat captain/salvor
50 ton USCG Master
NJ Boating College- Lead Instructor
Big time hottie crabber

Last edited by Capt. Debbie; 02-13-2014 at 12:10 PM.. Reason: Additional info
Reply With Quote